A device for use in applications requiring special water discharge patterns, directional spray, or other unusual
discharge characteristics, is known as a
What is the minimum flow rate required for the most hydraulically remote Class I standpipe?
For an Extra Hazard Group 1 remote area of 2,500 ft2 (232.25 m2) using fire sprinklers with a coverage area of
92 ft2 (8.547 m2), how many gallons per minute of water are required per sprinkler?
Annual testing for a 1,500 gpm (5,677 L/min) at 80 psi (1.4 bar) fire pump supporting an attached sprinkler system
demand of 1,800 gpm (6,813 L/min) at 100 psi (6.9 bar) is being conducted. The flow test of the fire pump must
achieve what minimum flow rate and discharge pressure?
How much pressure is lost to friction as 1,200 gpm (4542 L/min) travels through 200 ft (61 m) of 5 in. (130 mm) schedule 40 steel pipe with a C-factor of 120?
For an Ordinary Hazard with a design area of 1,500 ft2 (140 m2), what is the minimum number of standard pendent sprinklers required?
For a hydraulically calculated light hazard area under a mezzanine constructed of 2 in. (50 mm) x 14 in. (350 mm)
combustible solid wood members spaced 4 ft (1.2 m) on center, what is the maximum protection area for standard
upright spray sprinklers?
How much pressure is lost due to elevation in water flowing in a pipe from 6 ft (1.8 m) high to 15 ft (4.6 m) high?
What is the maximum distance an underground main can be installed under the building to the riser location without
additional requirements?
What is the correct number of sprinklers to calculate on a branchline for a building with an ordinary hazard
(nonstorage) occupancy, a roof slope of a rise of 3 units in a run of 12 units, and with sprinklers spaced
11.5 ft (3.5 m) on center along the lines?