Questions # 1:

The distance between a hanger and the center line of an upright sprinkler shall be no less than

Options:

A.

3 in. (75 mm).

B.

4 in. (100 mm).

C.

5 in.(125 mm).

D.

6 in. (150 mm).

Expert Solution
Questions # 2:

Antifreeze systems that contain a backflow preventer between the antifreeze piping and the wet pipe system must be

equipped with

Options:

A.

a relief valve.

B.

a sight glass.

C.

an accelerator.

D.

an expansion chamber.

Expert Solution
Questions # 3:

What is the minimum temperature rating of ceiling sprinklers in roll paper stored at 15 ft. (4.6 m) or less?

Options:

A.

100°F (38°C)

B.

135°F (57°C)

C.

150°F (66℃)

D.

175°F (79℃)

Expert Solution
Questions # 4:

The minimum flow rate for the required forward flow test of a backflow prevention assembly shall be the

Options:

A.

listed flow rate of the device.

B.

maximum flow rate of the device.

C.

system demand excluding hose stream allowance, where applicable.

D.

system demand plus hose stream allowance, where applicable.

Expert Solution
Questions # 5:

What is the minimum exposed barrel length for a dry sprinkler barrel exposed to 50°F (10℃) when the discharge end is in an environment of -30°F (34℃)?

Options:

A.

3 in. (75 mm)

B.

8 in. (200 mm)

C.

16 in. (400 mm)

D.

18 in. (450 mm)

Expert Solution
Questions # 6:

A sprinkler system has been installed with 100 sprinklers. What is the minimum number of spare sprinklers to be provided?

Options:

A.

3

B.

6

C.

9

D.

12

Expert Solution
Questions # 7:

When backflow prevention valves are installed on existing pipe scheduled systems, the friction losses of the device shall be accounted for when determining

Options:

A.

residual pressure.

B.

system flow requirements.

C.

static pressure.

D.

system GPM requirements.

Expert Solution
Questions # 8:

What is the pressure at a sprinkler head with a flow of 33 gpm (125 L/min) with a K-factor of 5.6 (80)?

Options:

A.

15.2 psi (1.1 bar)

B.

22.3 psi (1.54 bar)

C.

34.7 psi (2.4 bar)

D.

54.8 psi (3.78 bar)

Expert Solution
Questions # 9:

A kitchen in a restaurant encompasses an area of just over 700 ft2 (65 m2) with 2-hour fire rated walls. Does this meet the definition of a small room?

Options:

A.

Yes, as the limit is 800 ft2 (74 m2).

B.

No, 700 ft2 (65 m2) is too large.

C.

Yes, as the walls are 1-hour fire rated.

D.

No, small rooms are only of light hazard occupancy.

Expert Solution
Questions # 10:

According to NFPA 13, for a high rise building sprinklered throughout, that has four stairwells, each with a standpipe and hose valves, and has a Class I standpipe system, what is the maximum flow rate required to be calculated?

Options:

A.

750 gpm (2,840 L/min)

B.

1,000 gpm (3,785 L/min)

C.

1,250 gpm (4,731 L/min)

D.

1,500 gpm (5,678 L/min)

Expert Solution